Assuming you live in the USA, the electrical code requires you to use the 80% rule when attaching a device that can be on for more than a couple of hours continuously. This means that with say a 32A device, you'd need a 40A circuit to hard-wire it. 80% of 40 = 32A. But, you mentioned a plug. There are NO plugs or receptacles rated for 40A, and if you want to plug it in verses hardwire it, the next available receptacle and plug arrangement is a 50A one. Code requires the receptacle installed to match the supporting wiring, so if you want a plug on it, you need a 50A circuit. Crystal clear? On a 50A circuit, using that 80% rule, you could plug in something as large as a 40A device that ran continuously. Wires always have at least a little resistance in them - IOW, the wiring will warm up like a light bulb or your toaster slightly when power is flowing constantly. Using something intermittently allows the wiring to cool off in between uses. Not the case when you use it continuously, so for a safety margin, code requires you to derate the circuit to 80% of the maximum.
The difference in cost between a 30 and a 40A EVSE isn't all that much, and if you want a plug, the cost for the wiring would be the same. IF you choose to hardwire it, though, you could make the circuit for a 40A load verses a 50A one. Your i3 will work just fine with a larger EVSE, but a larger one, should you decide you have the power and want a plug, could be as big as 40A, which might make your next EV charge faster (it wont' hurt the is, but it won't help, either).